Ok so to summarize....
A freezing evaporator can be caused by several different conditions.
A) Inoperable blower motor
B) Clogged filter or clogged coil
C) restriction in the metering device
E) low freon charge
F) improper compressor cycling
There is no low suction pressure cutout on the tahoe, only a low system pressure cutout.
If system charge has been verified to be correct, hi & low pressure's are within range (before the evap coil is frozen) there is plenty of air moving across the evaporator....
The culprit appears to be a faulty evaporator temperature sensor. Apparently this sensor is prone to failure and determines the cycling rate of the compressor to keep the discharge air a constant temperature dependent upon blower speed and temp of air entering the coil.
In the OP's case, it sounds as though, given all system components check out, that the evap temp sensor is keeping the compressor running too long and causing the evap coil to freeze up, because its simply running the compressor too long.
In my case, I feel as though its satisfying pre maturely therefore the discharge air is coldish but not ice cold. I still need to do verify my system charge with real pressure gauges, but Im fairly certain it's fine. I dont think my orifice is clogged, because the line becomes cold and sweaty directly after it but this will be confirmed when I get some real hi/low gauges on it.
Feel free to tell me if im way off on this one.